There is this industrial building where non-fused disconnect switches were specified and installed within sight of electric motors (pumps). Each pump is fed from motor control centers and protected with either MCBB or MCP.
The purpose of the disconnect is to service the equipment (pumps). Obviously, the disconnect will not open under short circuit conditions. Per NEC-110-9, as long as the switch is rated for the motor FLA or HP the installation is safe. As you can see, NEC does not require the non-fuse disconnect to have a fault current listing (which is the case, because a disconnect with no fuse has no kAIC rating, unless is installed in combination with a disconnect fuse upstream).
Now, a consultant for the owner says that the disconnect switches shall be fused where the short circuit exceeds 10kAIC. I don't agree. Because the disconnect is not intended to interrupt fault currents!
Do you agree?
Thanks.
Do you agree?
Thanks.