Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

When Does a Building Need to be Brought up to Current Code? 1

Status
Not open for further replies.

ZFL

Structural
Joined
Nov 9, 2005
Messages
7
Location
US
I have been working on an addition to a warehouse. The existing building is a rigid frame with z-purlins. Today, the client informed me that they were removing the roof from the existing building and replacing it. Does this mean I need to bring the roof framing up to current code? Under what conditions must an existing building be upgraded?

Thanks
 
If your using IBC 2003, see chapter 34. If what they are removing is not structural and they are replacing with like kind...no problem. If not like kind, then as long as you don't increase the load in any member by more than 5%..no problem. If you discover that a structural component is deficient, during the repair, that member has to be broght up to the new code.
 
Forgot to add....If the load in a member is increased to greater than 5% but it still has capacity per the new code, it does not have to be brought up to the new code.
 
Thank you for the code reference twinnell. Here's a follow up question for you:

Section 3403.2 states "Where repairs are made to structural elements of an existing building, and uncovered structural elements are found to be unsound or otherwise structurally deficient, such elements shall be made to conform to the requrements for new structures."

What is the definition of "structurally deficient"? I believe that this building conformed to the code that applied at the time it was built, but calculations show that the purlins and the rigid frame do not meet the current code. Does this make them "structurally deficient"?
 
Structurally deficient in terms of the original building code. Or deficient by engineering judgment. For example, if you see steel that is highly corroded or steel connections that appear to be grossly inadequate. You don't have to check every member but if you or someone else sees something that is questionable, it needs to be checked and brought up to code if needed.

I have worked with some people that put blinders on when they enter a building they are doing an addition on. They head straight to thier area of design, inspect it, and walk out without seeing anything else. If they don't see it, it isn't deficient.
 
Status