Thank you for the response. After a quick read of the code, I only see a few areas where the maximum seismic load effect, Em, and the system overstrength factor is specifically required. The only areas I see are for collector elements, 1620.1.6, elements supporting discontinuous walls or frames, 1620.1.9, and certain components of light framed cold formed steel walls, 2211.7.2. That's all I can see. I was originally thinking that sections 1617.6 and 1617.1.2 were specific requirements to use the overstrength factors. This is apparently incorrect. So if I have a braced frame in design category C with R=3 (not detailed for seismic), then I can design the frame braces, beams, and columns, and all of their connections for the seismic load E (not Em). I can completely ignore the overstrength factor listed as 3.0 in table 1617.6 unless I run into the specific cases mentioned above. I guess the overstrength factor, even though it is listed prominently in table 1617.6, really only gets used in a few rarely encountered conditions as listed above.