Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

What level to set CO sensor in a coal silo to detect fire?

Status
Not open for further replies.

SA07

Electrical
Joined
Feb 22, 2018
Messages
380
Location
MU
Hi
Can you please confirm the level? Thanks
 
Not sure about fire detection, but worker safety requires something like this.
29CFR1917.24(a) said:
Exposure limits. The carbon monoxide content of the atmosphere in a room, building, vehicle, rail car, or any enclosed space shall be maintained at not more than 50 parts per million (ppm) (0.005%) as an eight hour average area level and employees shall be removed from the enclosed space if the carbon monoxide concentration exceeds a ceiling of 100 ppm (0.01%).
 
@SA07,
Set your CO monitor at 12.5% LEL. That way your silo gets the warning when concentrations get near the explosive limit.
 
I don't know about the source, but (way back) I was taught that 0.2% can kill you in 30 minutes.

So strange to see the singularity approaching while the entire planet is rapidly turning into a hellscape. -John Coates

-Dik
 
Thanks Parchie
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top