what is the minimum permissible aileakage rate for low pressure HVAC system? please can anybody help

Status
Not open for further replies.

tcihvacff1

Mechanical
Joined
Jul 2, 2012
Messages
49
Location
QA
please reflect your experience on this & i would appreciate if some one give me the procedure of doing air leak test...Thanks!
 
Check SMACNA for leak testing and proceedures.
 
yep willard3! i know that, but can u help me by mentioning the appropriate SMACNA version...
 
You may have to do some search yourself.
 
Smacna does print several books, but I think the one you need is the 'HVAC air duct leakage test manual'. Well, seems almost obvious when you write it out like that.
 
Without much research, I'd guess the minimum permissable leakge would be zero. Doubt that would be in the SMACNA manual.
 
You are allowed a certain percentage of leakage based on the pressure class and seal class of the ductwork in question. For example, seal class B ductwork allowable leakage rates are more stringent than seal class C. This info is in SMACNA, as mentioned above.
 
SMACNA provides maximum leakage. I'd also recommend looking at ASHRAE 90.1 for maximum leakage if you have to follow any energy code.
 