simple question ?
1) how many of these 20' sectiona are there ? is it a one off or a continuous tray ??
2) but the double trapeze are 8' apart ... does that mean that 1 20' cable tray is support by two supports 8' apart ?
3) if so, then if 20' weighs 410 lbs, then each support is carrying 205 lbs.
4) based on your sketch, 75% of the load goes to the LH support, and 25% to the RH one
5) 5/8" threaded rod is good for this load
6) the upper beam (B22A section ??) is taking this load into the I-beam. it sees two loads, 42" apart, and reacts them where it connects with te I-beam (not well defined). the maximum moment in the channel beam is at the LH support. since it's about 6' long, you should include the weight of the channel, about 24 lbs, as a distributed load.
7) how do the attachments to the I-beam feel about the load applied ? probably not a problem, but a question that needs answering.
8) how will the I-beam feel about he loads applied ? again, probably not a problem, but ...
9) this response started when you wee able to define a load requirement, rather than asking what the maximum is.
10) if you don't like our free answers, you're welcome to ask someone else ...
Quando Omni Flunkus Moritati