What is PBV? 1

Status
Not open for further replies.

carnahanad

Structural
Feb 4, 2010
44
Hello,

I'm a structural engineer and two electrical engineers showed me a detail of their generator pad that had a note that read something like, "...95% proctor test or 55psi PBV." Can anyone tell me what PBV means?
 
Replies continue below

Recommended for you

It is probably a reference to a "plate bearing value". The specification is poor in that the two parameters refer to two completely different things....the "95% proctor test" should read something like: Compaction under the pad shall achieve at least 95% of the maximum dry density as determined in the laboratory by the "Modified Proctor" method (ASTM D1557).

The 55psi PBV should be stated something like: the bearing soils shall have a minimum bearing/penetration resistance of at least 55psi when determined by (whatever test should be referenced in your area).

The first reference is to in-place compaction or density, while the second reference is a material stability criterion.
 
Ron,

That makes a lot of sense! I really appreciate the input!
 
If PBV means plate bearing value, 55 psi seems like pretty soft stuff, something like standard proctor 3-4 points wet of optimum, or bearing capacity failure under the heel of a large man's boot and deep ruts under a bicycle tire.

See pp. 17-23:


Regards,
DRG
 