Please see info below
1) drive type and manufacturer: VSD Schneider ATV630C25N4 250 kW 380-440 V
2) motor type and manufacturer (and possibly rating), Submersible Pump Saer S 302 A-4/A Impeller stainless steel 220 kW 400 Vac Duty point 350 m3/hr 13 bar 50 m cable directly connected to motor
3) cable type and manufacturer, single core
4) how the cable is attached (at both ends), directly connected to motor, directly connected to VSD
5) whether the cable is shielded - and how, Non shielded
6) whether there are other nonlinear loads and/or sources connected to the same bus as the drive input, 1 soft starter for another pump
7) how tolerant the process is of small torque/speed variations, and : do not know
8) what specific insulation materials are used in the motor winding(s). according to supplier PE+PA
We want to know after what length of cable it is recommended to install a sine wave filter? Some people are saying 20m, 100m, 100feet
Our motor has just failed. The insulation winding is faulty with earth just after 700 hrs of operation.
It seems a VSD is not appropriate for submersible pump. What is recommended acceleration, deceleration time?
Any other precautions to take?
What other means can we use to operate the pump? direct on line, soft starter, auto transformer, star-delta?