I assume the original design main steam temp is 1060 F , and this is a gas fired combined cycle plant.
Exceeding design temp by 100F will:
a)temporarily improve steam turbine cycle efficiency, if increased seal leakage did not develop
b) the rate of creep life exhaustion at 1160 F will be more than 20 times faster than at design temp of 1060 F, and the rate of oxidation of ferritic superheater tubes also accelerates
c)probably violate asme B31.1 rules for not exceeding max temp for which there is publised an allowable stress for listed alloys
d)exceed the steam turbine mfr's max permitted inlet steam temp, and put their warranty in jeopardy ( by the way, they are monitoring these temps and will let you know it, someday )
e) exceed the max assumed metal temp the piping designer used when designing the pipe supports- if the pipe hit a solid bumper during its expansion, the pipeline stresses would increase dramatically, and stresses at the HP main steam valve to pipe weld would be excdessive.
f) turbine seals may have excessive wear due to expansion effects.
g) loss of effiency may be due to seal wear and also solid particle erosion SPE of the 1st stage due to exfoiliation of oxide particles formed in the HP superheater tubes due to the overheat, and worsened by throtlling of the HP throttle valve. 5% loss of HP efficiency due to SPE is not uncommmon.
h) such overheats are absolutely verboten in some parts of europe, and to avoid this during startups of gas fired combined cycle plants, some eu plants use final attemporators on the main steam and hot reheater pipes. Such overheat seems to be common practice in the US, though.