I generally agree with the published guidance pointed to in this thread, and particularly perhaps when directed to what I suspect are common very small service connections to e.g. a small diameter distribution water main (like 8” as the original inquiry). I will make the comment, however, that if is desirable to make a significantly larger (e.g. originally unanticipated) tap into e.g. a much larger new transmission main, I would think there could be a rather significant difference in logistics and/or cost to make the connection depending on the method chosen. In the case of a “dry” connection, it might be possible to simply cut a sizeable hole in the pipe with common tools, assemble a tapping sleeve or saddle over the hole and around the pipe (as may be required for structural strength/reinforcement etc.), then lay the branch piping (also with common, simple tools/equipment) not much unlike other pipe work. In the case however of a larger branch size wet tap under pressure, this of course requires quite heavy, complex, and specialized equipment and expertise that may not necessarily be as readily available to all contractors and utilities.
Also, e.g. if small taps and corp stops/service lines etc. are installed in the dry and prior to pressure tests, the pressure rating and capabilities of all elements/appurtenances then under pressure in the eventual test should probably be considered (I have heard that some modern mains and joints etc. are capable of, and now sometimes being subjected to, very high pressure acceptance tests, that can be well beyond e.g. the seat rating of at least some valves or corporation stops, etc.)