Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Welding rebar 1

Status
Not open for further replies.

SperlingPE

Structural
Joined
Dec 27, 2002
Messages
591
Location
US
I have situation requiring welded rebar splices.

1. Is this a pre-qualifed weld?
2. If not pre-qual, what is required?
3. What type of splice would you recommend?
a. bars side by side
b. bars welded to a plate
c. butt splice
 
Unless the rebar is stipulated as being weldable, you likely have to do a metalurgical analysis and determine the carbon equivalency.

Dik
 
It is new construction. Rebar is specified as weldable.
 
Try the rebar manufacturer's web site.
 
AWS D1.4 covers welding reinforcing steel.

I recommend you only allow ASTM A706 rebar to be welded, not ASTM A615.

If you have to weld the rebar, I think a lap splice would be my first choice, however, that is highly dependent on the specifics of your situation.

I would first check into mechanical splices before looking at welding. There are many that are capable of developing 125% of the specified yield strength of the bar.

Good Luck.
 
As mentioned AWS D1.4 is typically the applicable code. Also, A706 has a W on that indicates weldable.
1) The only weld pre qualified by his code is a fillet. This would only apply to T connections.
2)The WPS will need to be qualified by testing. The welder will also need to perform a certification test.
3)Splice is dependant on application.
 
thanks for the assistance
The weldable rebar (A706) is already specified if welded splices are used.
AWS D1.4 is on the way.
Contractor is reconsidering the use of mech. splices because of the required testing and welder cert.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top