truckdesigner

Structural
Oct 19, 2009
42

In normal circumstances we specify a Complete Penetration Butt Weld with this type of thing, but I am investigating in another instance simply specifying a 6 or 8 mm fillet weld instead.

I have attached a computation of the scenario. Could someone please take a look at it and offer me any advice, confirm that it is correct etc.

Any advice greatly appreciated.


Regards.

 
Replies continue below

Recommended for you

You forgot the shear calculation from Fh at the weld. Your Fr value is not right as it should include the max tensile stress from tensile force and bending moment and the shear value from Fh.
 
Hi again

I did a quick calculation using the Roymech site I posted previously and found that your 6mm weld will fail.
I used the table of "bracket weld subject to bending and direct stresses" cases 1 and 3 and the formula for stresses in the weld at the far right of the table.
I get a resultant stress of 484N/mm^2 and compared this with the design strength of fillet welds which appears to have a maximum of 280N/mm^2 depending on material grade.

desertfox
 
Hi Again

I also noticed that in your calculation that you have used the area of 30000mm^2 then after dividing it into the loads on your lugs,then you've compared those values with a safe load per unit length, so the values you're comparing have different units ie:-

kN/mm^2 and kN/mm which cannot be correct.

desertfox
 