Assuming you're governed by US codes:
Flare bevel and flare vee welds are PJP welds. If you look in AISC 360 table J2.2, they show the effective weld sized for flare bevel and flare vee welds as a function of process, position, and radius. This information is also in AWS D1.1 Table 2.1. Depending on those variables, the weld size (formerly known as effective throat) ranges from 5/8R to 5/16R. The rule of thumb I was taught, although I can't cite a source, is that the outside radius of A500 tube is typically 2 times wall thickness. So, to KootK's point, the code expects a substantial void behind the weld - you just can't reliably penetrate into the acute angle at the root of the joint. It's on the engineer to design for that throat.
As for how the contractor establishes that throat, they have two options. they can use a prequalified joint (B-P11, B-P11-GF, or B-P11-S) and use the somewhat conservative weld sizes specified (5/8R, 3/4R, and 1/2R respectively) or they could qualify a procedure, which would require them to macroetch sample welds to establish the weld size.