shaneelliss (Structural) said:
25 Mar 14 16:09
Thanks all for the comments. I am doubling a channel because one channel is already in place but it is not enough, by about half. So I am simply adding an identical channel next to it. Some steel grating is resting on the channels and theoretically each channel will take half the load and they don't need to be connected at all. As dhengr points out, I just want to connect them to brace each other and to act mostly in unison. I think the take-away I am getting here is that I can't really just have them do a surface weld at the seam, that I must have them create at least a one sided bevel for even the small welds I would like to see.
I'm going to strongly disagree with you - not exactly with the intent of your solution, but your execution is gong to break.
Failure mode will likely be: Assume you grind a weld prep "v" into BOTH sides of the joint on both top and bottom sides evenly and perfectly. And then you weld both sides together evenly and perfectly so there are no stresses or uneven heating and cooling and exactly even penetration on both sides of both channels evenly on both top and bottom exactly offsetting each other so - yes! - both beams will carry half of the load.
If that all happens, then - yes! - both beams split the loads.
Ain't gonna happen in real life. Worse, what will happen in real life is that the upper weld bead WILL vary unevenly in height above the flat top of the two channels, and in penetration below both sides of the two channels.
Now, when uneven loads are put on the gratings ABOVE the uneven weld above the two channels, the higher of one side of the one of the stitch welds is going to get ALL of the concentrated loads not from just the local weight, but all of the weight on the whole section of grating. It has to: That single little location is the only place where the grating touches the channel. That one half of one stitch weld is going to yield (force the half-beam down) or break.
Once that happens, your two channels begin reacting unpredictable as each section yields to a higher stress than it can handle. (You've already concluded that you need to double the existing channel to handle the expected loads, right?) so, this combination of single point yielding has noting really to stop each half-weld (of the two stitch welds) from catching all the actual loads at that point. The final will have the two half-beams sagging enough so they share the residual load in tension - if the two ends of the two channels are restrained by bolts or angle iron connections. If one is "tighter" than the other, then it will try to stop all of the load itself and likely fail. Then, all of the load falls to the remaining beam - which is also expected to fail.
Better, in my opinion, is NOT to weld the two beams. In particular, I strongly recommend NOT welding ANYTHING on the upper surface of either back-to-back channel! Rather, drill through a 5/8 or larger high tensile bolt every 2-1/2, 3, or 3-1/2 feet, and bolt the two channels together.