Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Waterproofing Exterior Suspended Slab on Steel Framing

Status
Not open for further replies.

ekelley

Structural
Mar 26, 2010
3
Is there a need to waterproof an exterior suspended concrete slab on top of steel framing? The architect is requesting a waterproofing membrane and 4" conc topping on top of 6" structural slab to protect structural steel framing below. I have not heard of this as an issue. It changes the design loads on the steel framing significantly. The structural system is a 6" structural slab on steel framing. The floor supports both interior and exterior spaces above although there is a roof above the exterior space. The space below the floor is all exterior, but has a ceiling below bottom of structural steel. Is there a need for waterproofing to protect the steel framing below? Any other options to accomplish this without 4" topping slab?

Thanks
 
Replies continue below

Recommended for you

It's a really good idea... take a gander at the Algo Centre Mall collapse... I've often used Duradeck type of membrane for walking surfaces for boat houses or a proper EPDM or anyother single ply membrane...

Dik
 

I never heard of that one - of course, because for some reason,, all news happening in Canada is suppresses here in the good ole USA>

The definition of a structural engineer: overdesign by a factor of 1.999, instead of the usual 2.
 
I've specified a silicate sealant before such as Concrete Treat for situations like yours to eliminate the need for a topping slab and membrane. It works great. I probably wouldn't use it on an slab without a roof with heated space below but for an elevated garage, or slab without heated space below, absolutely.

 
If you use a single ply, I would use densdeck adhered to the structural slab and tapered insulation/blocking if slope is needed. Much lighter than concrete. Single ply roofing directly on concrete wouldn't be my first choice.
 
I would always waterproof it - otherwise you get a rusted mess later on.

We typically use a traffic bearing waterproofing system similar to Pedagard (by Neogard) found here.

Or we use what you describe above as a membrane waterproofing system with a concrete topping/wearing surface.

One we've used in the past is by Carlisle - found here and here

There are other companies for both offering similar products.
 
Status