Is there a need to waterproof an exterior suspended concrete slab on top of steel framing? The architect is requesting a waterproofing membrane and 4" conc topping on top of 6" structural slab to protect structural steel framing below. I have not heard of this as an issue. It changes the design loads on the steel framing significantly. The structural system is a 6" structural slab on steel framing. The floor supports both interior and exterior spaces above although there is a roof above the exterior space. The space below the floor is all exterior, but has a ceiling below bottom of structural steel. Is there a need for waterproofing to protect the steel framing below? Any other options to accomplish this without 4" topping slab?
It's a really good idea... take a gander at the Algo Centre Mall collapse... I've often used Duradeck type of membrane for walking surfaces for boat houses or a proper EPDM or anyother single ply membrane...
Dik
I never heard of that one - of course, because for some reason,, all news happening in Canada is suppresses here in the good ole USA>
The definition of a structural engineer: overdesign by a factor of 1.999, instead of the usual 2.
I've specified a silicate sealant before such as Concrete Treat for situations like yours to eliminate the need for a topping slab and membrane. It works great. I probably wouldn't use it on an slab without a roof with heated space below but for an elevated garage, or slab without heated space below, absolutely.
If you use a single ply, I would use densdeck adhered to the structural slab and tapered insulation/blocking if slope is needed. Much lighter than concrete. Single ply roofing directly on concrete wouldn't be my first choice.
I would always waterproof it - otherwise you get a rusted mess later on.
We typically use a traffic bearing waterproofing system similar to Pedagard (by Neogard) found here.
Or we use what you describe above as a membrane waterproofing system with a concrete topping/wearing surface.
One we've used in the past is by Carlisle - found here and here
There are other companies for both offering similar products.