I've got a project where a precast double tee parking garage is intended to serve as a "roof" over an occupied space below. The question I have is how to properly detail the deck to be waterproof.
The two ideas I've seen are:
Option 1
1. On the double tees, place a 2 to 3 inch concrete topping as a composite structural slab over the tees to serve as a diaphragm.
2. Over this topping, place a waterproof membrane with a thin protection board (1/4" perhaps).
3. Over the waterproofing, place a layer of rigid insulation (4")
4. Over the insulation place a 4 to 5 inch thick concrete wearing surface - basically a pavement of sorts with sawed joints.
Option 2
2. On the topping place a layer of rigid insulation (4")
3. Over the insulation place a 4 to 5 inch thick concrete wearing surface - basically a pavement of sorts with sawed joints.
4. On the wearing surface place a traffic bearing waterproofing system (Autogard by Neogard or similar).
Are there any problems with the above systems and are there any other methods that others have used for this situation?
Thanks,
Option 1
Option 2
Thanks,