mathmday
Civil/Environmental
- Jul 7, 2009
- 7
I currently have a Client that is installing water main extension(s) to rehabilitate an existing system and is encountering difficulties that I believe are beyond his control. Any advise on means or meathods that he can utilize to mitigate this problem would be greatly appreciated, and ideas of other potential causes of the problem.
Existing System - 4in dia cast iron, leaded joints every 20', unclorinated, wells provide source water, approximately 40% loss of produced water due to leakage.
Improvements - 8in dia C900 PVC, cast iron fittings, flushing / chlorination / pressure and bacteriological testing being performed in accordance with the appropriate AWWA standards.
Problem - Currently he has installed approximately 6,750 LF of pipe. Through the course of construction this season he has had 27 failed Bac-T tests due to coliform hits. This equates to a failed test for every 250 LF of pipe installed.
Hypothesis - Due to the abnormal amount of tests indicating the presence of coliform without a significant and measurable amount of chlorine being utilized in the disinfection process, as indicated by the residual, we hypothesize that either: pressure transients induced by the specified flushing procedures or other systemic causes are providing a pathway through existing pipe deficiencies, or biofilm containing coliform is being stripped from the existing pipe walls into suspension thus causing difficulties passing our bacteriological tests.
Existing System - 4in dia cast iron, leaded joints every 20', unclorinated, wells provide source water, approximately 40% loss of produced water due to leakage.
Improvements - 8in dia C900 PVC, cast iron fittings, flushing / chlorination / pressure and bacteriological testing being performed in accordance with the appropriate AWWA standards.
Problem - Currently he has installed approximately 6,750 LF of pipe. Through the course of construction this season he has had 27 failed Bac-T tests due to coliform hits. This equates to a failed test for every 250 LF of pipe installed.
Hypothesis - Due to the abnormal amount of tests indicating the presence of coliform without a significant and measurable amount of chlorine being utilized in the disinfection process, as indicated by the residual, we hypothesize that either: pressure transients induced by the specified flushing procedures or other systemic causes are providing a pathway through existing pipe deficiencies, or biofilm containing coliform is being stripped from the existing pipe walls into suspension thus causing difficulties passing our bacteriological tests.