Monjo,
I wish to take a step back here and look at your whole statement.
Your question, and indeed the responses, have centered on whether current limiting is a good or bad thing.
There is no doubt that with a variable speed Drive, Current limiting is desirable and indeed effective way of controlling the current to the motor.
my question centers more on
"Why are you getting these overcurrent trips in the first place?"
From my experience with VSD's they have very good current limit control, and an inherent part of engineering the system is to specify and set the current limit function at a level that is appropriate to the Drive, the Motor and application. (taking into account the comments by Aolalde, and others)
Usually the Overcurrent trip level is set a reasonable margin, outside this Limit value, and as long an nothing fails the the question of trips has been a "Moot Point"
Maybe your Conveyor Application has some very sudden impact loadings, leading to fast motor decelerations, however the speed of most control functions in most modern VSD's that I have dealt with, are usually fast enough to handle this.
I think you should be asking questions such as
"Is the trip a thermal overload ( I^2 T ), a Timed overload or an instantaneous overcurrent (IOC)?
"What level is the IOC setting with respect to the Drive nameplate? (I would be aiming for the area around 2.2 PU)
"what level of current can the drive handle in an IOC situation"
"Is the Overload setting based on the Drive current capability or the motor capability ?"
"At What Value do you plan to put the Current limit?" (1.5 PU of motor rating is a good starting place)
"Can your drive impliment a 'Tapered Current Limit' that will give you high torque for breakaway from standstill and reduce as the speed builds up?"
I would base the IOC setting on the Drive rating, as motors tend to ride through IOC's better then Drives.
I would base the Current Limit and the thermal overload on the motor nameplate value. ( after checking that the Continuous rated current of the drive exceeds the continuous rated current of the motor)
Finding answers to these questions should lead to a proper engineered application that should give trouble free operation.
I am just concerned that there is some other outside influence causing the trips and that placing the Current limit function at a more conservitave setting would restrict your application, and hide a more insideous problem that will come back to haunt you at a later date(most likely at 2.00am new years day or some other inappropriate time like that).
Regards
Tom