Good day,
I have a question on voltage changes in the supply side of some wiring.
One leg that comes into the panel reads 115 VAC the the other 126VAC when no load is applied. The grounds are connected together and connected to an earth ground rod. The neutrals are connected via a bus which are connected to the primary panel via a neutral cable.
When a load (such as a pump or heater) is put onto either of the incoming power legs, the voltage changes to 69 VAC on one leg and 170 VAC on the other leg.
Anyone have a suggestion on where to check? I'm completely stumped.
Thank you.
I have a question on voltage changes in the supply side of some wiring.
One leg that comes into the panel reads 115 VAC the the other 126VAC when no load is applied. The grounds are connected together and connected to an earth ground rod. The neutrals are connected via a bus which are connected to the primary panel via a neutral cable.
When a load (such as a pump or heater) is put onto either of the incoming power legs, the voltage changes to 69 VAC on one leg and 170 VAC on the other leg.
Anyone have a suggestion on where to check? I'm completely stumped.
Thank you.