Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Voltage Drop for Single Phase system

Status
Not open for further replies.

JatTiw

Electrical
Dec 10, 2002
47
HI,
For single-phase system (Phase & neutral), the load is at ‘X’ distance form the source and to calculate the voltage drop in the cable, shall I use 2X distance (X-for phase wire + X-for neutral wire) or just X-distance?
 
Replies continue below

Recommended for you

You should use 2 time the distance "X" for this caculation
 
It depends on the data you are using for calculating the voltage drop. Some data sources are for circuit feet, some are for conductor feet. In your case circuit feet are half of conductor feet.
 
It is NOT a given that the neutral wire will be of the same gauge as the phase wire.

If dissimilar, the wires will have different impedances, and voltage drop 'out' and 'back' need to be done separately.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor