Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

voltage drop calc - help

Status
Not open for further replies.

EIT231

Structural
Joined
Apr 21, 2010
Messages
8
Location
US
hey there and thanks in advance -

I found this article

and this problem: (480v branch ckt - uncoated copper)
Determine wire size Run a stranded copper wire 200 ft at 20A.
you can use the following method. To complete the numerator, multiply as follows: 1.73 x 212.9 ohms x 200 ft x 20A = 89371.2 Dividing the 89371.2 by the acceptable voltage drop of 14.4V gives you 6207 circular mils.

Where is the 212.9 Ohms from?

thanks
 
guessing from the info you provided the 212.9 ohms is the impedance of the line in ohms/ft.
 
Sounds like an awful high impedance for 1 ft of wire!
 
thanks -
it is a typo -

2 x .866 x 12.9 (k for cu) x 200ft x 20A = 89371

89371/14.4 (VD branch ckt - .03 x 480) = 6206cm

thanks folks


 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top