I agree to jghrist. The voltage drops do not affect directly the shc current value.
Basically and very much simplifying, the short-circuit reduces to a circuit formed by an equivalent impedance connected to the source (it is a "short" circuit). The shc current is basically I=U/z. The value of z depends of distance between the source and point of shc; the distance is not to be understood as "length" but as number and arrangement (series, parallel) of impedances that give/compose the equivalent impedance.
For your case, the impedance is not only a series impedance given by the cable's impedance (long length, z=L*z0) but also by the impedances of the succesive loads along the distribution cable which are to be considered in parallel connection (if the loads are connected to the distribution cable/network in the moment of shc). However, the impedance at the last point is bigger than the impedance at transformer side, even considering the parallel connected impedances (zpar=sum(zi)/n, i=1...n), so the shc current will be lower.