Vibration check for timber floor 1
m_struct
NZ
When checking a timber floor for vibrations, 1170.0 Table C.1 suggests 1kN point load at midspan with deflection less than 1 to 2mm.
For a timber floor, with say 20mm strandfloor on 240x45 @ 400 spanning 4m, how much load sharing would be reasonable? It is there a rule of thumb for this? Also, it is reasonable to take the 2mm deflection limit (not the 1mm)?
I would say spread it over three boards and consider them all fully effective. [Edit: misread your floor structure description]
Whether to use the looser deflection limit depends on how much a problem vibration is. Note that the check you're proposing to use isn't bulletproof. I'll try to find the reference that discusses it.
See the 1991 paper here: Thomas M. Murray "Building Floor Vibrations"
Apparently it was originally the 1mm limit, though the Murray paper suggests tightening that by a factor of four for commercial floors. Although that reads as a 'deemed to comply' sort of limit and a detailed check might give a less strict result.
BRANZ SR57 suggests 1.5mm for highly damped floors: see Table 1A
Thank you for that. I will have a read through those. Vibration papers also seem to be lengthy.
The condition in question is a residential floor in a single family unit. The member spans from perimeter wall to wall (4.3m) and has a 600mm that supports the first floor wall and roof above. The (dead load) point load at the end of cantilever, takes out the a lot of deflection, but is not considered in a vibration case, it is suggested to use just ψsQ.
Distributing the 1 kN over 3 members gives a 1.3mm midspan deflection. Again this is not considering any G, notably at the cantilever, which would act like a precamber. Can that G load (exterior wall and roof above) be accounted for - it is permanent dead load?
The Nash standard has the formula you want, there is an equivalent in an old timber standard as well but cannot remember the number.
In regard to load sharing, 1720.1 and 3603 address load sharing for a centrated loads in a grid system.
1720.1
G41
3603
k9
My numbers showing both g41 and k9 are about 60%.
The "1mm limit" is an extremely poor indicator of a low frequency vibration issue (i.e. floor system resonance under footfall), a 1mm (or other) deflection limit is a better indicator of a high frequency vibration issue (i.e. caused by high frequency vibration of plant or similar operating).
Unfortunately, because a deflection limit is typically easy to apply, as opposed to trying to understand and apply other more rigorous vibration assessment methods, it is wrongly abused/employed as a general vibration limit to identify both high and low frequency issues.
In addition to the load-sharing effect, if you're after a procedure suitable for timber floors, the recent BRANZ multistorey timber building design guide addressed the problem with a design method. It is freely available here, but you have to register