The answer to your question regarding total current harmonics is not simply determined by the VFD. The power network characteristics, transformer impedance, lead lengths, other loads, and VFD design all impact the resulting harmonics.
Many drive manufacturers have computer-based programs which will predict harmonic levels with remarkable accuracy when you input the above network characteristics. Some of these manufacturers will run the analysis without cost to you.
I would have this analysis done before adding anything in the way of extra cost to the system. As has been noted already, you may already be on the verge of overspecifying a solution. I agree with the earlier posters who suspect that a standard six pulse drive possibly with input reactors will meet your needs.