Suggestion to tmahan (Electrical) Aug 12, 2002 marked ///\\Jbartos is not correct. "Inverter Duty" is a term that is thrown about and tend to mean different things to different people (or motor makers).
///There appear to be definitions of those on web, e.g.
\\ What JBARTOS is refering to is a small secondary blower motor that provides cooling for the primary motor.
In the case of a 1HP 230V adding a blower would be very unusual (I think). Typically on a small application such as this you would simply upsize the motor frame depending on the speed range that was to be covered.
///If application or circumstances permit this upsize.\\The large frame would have a large thermal mass to distribute the heat generated.
///Yes and no, depending on the motor shaft load and motor speed for how long time.\\There have been many threads on inverter duty motors but a brief summary would be that the motor should be able to withstand any voltage spikes produced by the inverter. I would not spen much time worrying about the aspects of inverter duty or not.
///This is usually not advised.\\ (no doubt others will disagree but at 1 HP, so long as the motor is from a good supplier like AB, ABB Toshiba... you should be fine)
///It depends on application. This is why special motor designs are in existence.\\With regards to putting the unit in true torque control. It will not cause any further current draw. By adjusting the magnetization current and load current open loop control may solve your problems with the overload. It will without a doubt give you much more torque for a given current level and much greater speed control.
///Could you clarify how the "...magnetization current adjustment and load current open loop control solve the problem of overload and simultaneously give much more torque..."\\