I am looking to find the best voltage for MOTOR-VFD solution at a 800-1000 kW. What is the Voltage trend worldwide for this power? 415 V, 690V or 11 kV.
Tanks
Peter
Tanks
Peter
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
A large number of motors (maybe just IEC) are dual voltage 400/690V.
The IEC motors typically use 3 windings and offer dual voltages by either a star or delta connection. The voltage ratio is 1.73:1
NEMA motors use 6 windings and offer dual voltages by either a series or a parallel connection. There is a buried connection and the motors cannot be changed from the normal star to delta in the field. There are also some legacy delta motors with 3 buried connections.
The voltage ratio is 2:1
The connection diagrams for a twelve lead generator give a good overview. The diagrams with the windings in series are applicable to most IEC motors.
The diagrams with a star point are applicable to most NEMA motors.
As always, there are exceptions. Even this statement has exceptions.
respectfully