We have had tripping problems on a particular VFD (old 400hp Emerson drive system) for a few months now. Unfortunately, the trip condition shows no diagnostics to help identify the problem.
I used a datalogger yesterday to monitor and record various electrical parameters and found that the current in the "A" phase 5% of that in the other two phases and the ground cable is carrying a current equal to that of the other two phases as well.
I am surprised that our clamp on ammeter did not pick up this unbalance. Without further analysis I suspect that the ground fault relay on the ground conductor senses the imbalance, resulting in the trip condition.
Aren't those clamp on meters true RMS?
I used a datalogger yesterday to monitor and record various electrical parameters and found that the current in the "A" phase 5% of that in the other two phases and the ground cable is carrying a current equal to that of the other two phases as well.
I am surprised that our clamp on ammeter did not pick up this unbalance. Without further analysis I suspect that the ground fault relay on the ground conductor senses the imbalance, resulting in the trip condition.
Aren't those clamp on meters true RMS?