Dear all,
I have a similar case to that discussed in thread237-286989
but the generator is definitely oversized in comparison with the inverter (Customer says 200 kVA ?, while our machine is 58 kW total where VFD inside is 18.5 kW) and we are running at low voltage (415 V 50 Hz).
Randomly we get an alarm from inverter due to DCbus voltage changing too much.
My idea is to install a DC reactor on the VFD connected to one side of the DCbus (the VFd is a Omron E7 model, it has terminal blocks for that and the DC reactor is suggested in the operator manual in order to improve power factor).
In your opinion is the right thing to do?
Thank you.