I am designing a pipeline project, where the system is very weak, so that we have to use VFD to start the biggest motor(5000KW).
Utility company informed the client that even VFD starting would cause voltage drop on the consumer bus and on the utility bus, which would exceed the flicker limits.
But I did load flow study. with all the loads running, the volatge drop is only 3%. There is no voltage drop on utility side.
Since while VFD starting, the power factor is 0.95 and current is limited only around 100%FLA. Theoretically, the voltage drop should be the same as under normal running condition.
However, ETAP gave me the different results. Whenever I started motor by 100% or higher, i always got much higher voltage dip on the system, which didn't make sense to me.
I presumed that ETAP cann't model VFD starting properly.
Any inputs would be appreciated.