VFD Power Modeling

Status
Not open for further replies.

wzrdstrm

Electrical
Sep 1, 2007
8
Team,
I'm trying to develop a mathematical relatiionship for the HP(or KW)for a Motor controled by a VFD. The motor is a 1150 HP 600VAC, 40 HZ 6 pole motor. I have a theoretical model showing a linear relationship from 0hz to 40hz. HP is constant to a point after that, I know. I'll have different motors later. The idea is to control the amount of KW used for power management (below rated HZ). Basically, I will be given a KW limit and will have to determine the speed necessary to reduce the motors KW to at, or just below this limit. Using the theoretical model, I can use the equation for a line, but was looking for a mathematical formula, such that I can just switch motors and get the data for the new motor (i.e. switching from 1150hp to 1500hp).
 
Replies continue below

Recommended for you

wzrdstrm,

Compositepro is right. For example, if your load is a pump in a variable-flow system, horsepower at a given speed will depend on the position of the control valves (i.e., how much flow is being demanded).

Rather than trying to model the drive/motor/pump system, which can be extremely complex and subject to lots of measurement error, why not just put a PID controller or PLC in with a watt transducer as input? That could be arranged to control the VFD to maintain whatever upper limit you have set at the time.

All this assumes you have a load that can be safely starved of power, of course... Fans, pumps, etc..., in HVAC systems that aren't critical might be adaptable -- what's your motor doing, anyway? If it were a sewage pump, it could get really messy...

Good on ya,

Goober Dave
 
Recheck if your VFD has the PID function or if you can control it by a torque adjusment fucntion inside. Other option is that you can use the the analog output signal configured as a Power or energy signals and with a small PID controller feedbak the analog VFD's speed input