Mike,
Thank you for the addition insight into the world of centrifuges.
If OSHA codes are adhered to, personnel safety should be a non-issue... but we both know that's not the real world. And so, there will be a time when someone will get entangled with the machine. And 5 minutes to stop is much too long. When it comes to personnel safety, the machine is usually sacraficed as necessary to get the thing stopped.
Some methods I've encountered over the years, include an eddy current clutch-brake with the brake very much oversized to produce the necessary braking torque.
On DC drives, I've seen the regen capacity doubled over the motoring capacity (bridge sized for twice as much current.
And on a few occassions, I've used Plug reversing under current limit control (VFD). This requires adding an encoder or zero speed switch on the centrifuge to sense when zero speed is achieved. No line regen occurs, and dynamic braking not required. But the motor-- now that's a different story. Since the inertial energy is dissipated as heat in the motor, it must be sized larger (over framed) or force-ventillated to get rid of the heat.
I don't have my copy of NFMA-79 here with me but I'll look on Monday to see if there isn't a breaking requirement. Seems I've seen a spec for centrifuges somewhere along the way.
Enjoyed the dialog.
jOmega