xj25
Electrical
- May 7, 2011
- 110
Hi,
I saw recently a peculiar system, this is a 3ph custom VFD + 4 induction motors in parallel. The motors are labeled Vn=600Vrms
The curious thing is that the VFD can work in an "emergency mode" supplied from a (really big) 48V battery.
They use that to allow moving the thing quite slowly to a "controlled" position even if power fails.
It puzzles me so big difference of supply voltage (600 to 48), but even so it makes the work quite well.
The VFD has no boost circuit or DC/DC, just typical PWM VSI.
I understand that a high current can be supplied by the battery to the DC bus (it uses a 200A breaker), but voltage is very low, and as far I understood, motor flux depends mainly on peak voltage (and freq.). In a vector controlled drive I understand that torque is proportional to flux and "load" current so torque should be quite low comparing the nominal voltage (48/600?).
Just want to know your opinion on the topic about how affects so big voltage change to the motor performance. Maybe there is some control strategy to overcome that?.
Regards
I saw recently a peculiar system, this is a 3ph custom VFD + 4 induction motors in parallel. The motors are labeled Vn=600Vrms
The curious thing is that the VFD can work in an "emergency mode" supplied from a (really big) 48V battery.
They use that to allow moving the thing quite slowly to a "controlled" position even if power fails.
It puzzles me so big difference of supply voltage (600 to 48), but even so it makes the work quite well.
The VFD has no boost circuit or DC/DC, just typical PWM VSI.
I understand that a high current can be supplied by the battery to the DC bus (it uses a 200A breaker), but voltage is very low, and as far I understood, motor flux depends mainly on peak voltage (and freq.). In a vector controlled drive I understand that torque is proportional to flux and "load" current so torque should be quite low comparing the nominal voltage (48/600?).
Just want to know your opinion on the topic about how affects so big voltage change to the motor performance. Maybe there is some control strategy to overcome that?.
Regards