120V 60Hz is single phase, you cannot use a VFD on the vast majority of single phase motors. Those that can be run from a VFD would not be suitable for a band saw.
You would have to SERIOUSLY over size a UPS to be able to deal with the starting current of an AC motor on something like a band saw. That would be very expensive.
By the time you get done with all the rigamarole it will take, it will be far far easier to just go out and get 230V 50Hz motors for them. If not, just get a transformer to step the 240V 50Hz down to 100V 50 Hz, which gives them the same V/Hz ratio as the motors were designed for. The motor will run 20% slower, but will produce full torque and not over heat or (shouldn't) over load.
Or buy new small band saws over there that are designed to work over there, saving the shipping cost as well. Sometimes people try too hard to insist on making electrical stuff work in foreign countries when it would be so much simpler to start fresh. They just don't understand what it means.