So I've got a bit of a tricky situation.
I've got a client with an industrial factory that was built in 1909 in a tidal zone on piles. The structure is essentially a dock, with wooden piles of unknown depth or quality into the soils below, the soils are also of unknown properties, so the existing foundation is impossible to justify via calculation.
Elsewhere in the same building, 8 years ago there was a load test to verify capacity for a 100kip machine.
The proposed machine they want me to design for is a 200kip machine, but it loads a few more piles than the existing 100kip machine. Obviously these piles are different than the ones that had been load tested.
They want to skip load testing for the new 200kip machine. What would you do? Should I design a slab and anchorage to the building and put on the drawings "EXISTING PILE CAPACITY TO BE VERIFIED BY OTHERS"?
I suppose in all of this, where does my responsibility end? I don't foresee any safety concerns if the piles were damaged by the weight of the machine, but it could be enormously expensive to repair any damage.
Should I walk away from the job?
I've got a client with an industrial factory that was built in 1909 in a tidal zone on piles. The structure is essentially a dock, with wooden piles of unknown depth or quality into the soils below, the soils are also of unknown properties, so the existing foundation is impossible to justify via calculation.
Elsewhere in the same building, 8 years ago there was a load test to verify capacity for a 100kip machine.
The proposed machine they want me to design for is a 200kip machine, but it loads a few more piles than the existing 100kip machine. Obviously these piles are different than the ones that had been load tested.
They want to skip load testing for the new 200kip machine. What would you do? Should I design a slab and anchorage to the building and put on the drawings "EXISTING PILE CAPACITY TO BE VERIFIED BY OTHERS"?
I suppose in all of this, where does my responsibility end? I don't foresee any safety concerns if the piles were damaged by the weight of the machine, but it could be enormously expensive to repair any damage.
Should I walk away from the job?