Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

vertical concrete box design 1

Status
Not open for further replies.

Vfigueroa

Structural
Joined
Aug 2, 2005
Messages
6
Location
PR
If a square concrete well is to be constructed on clayed soil enviroment, what forces should be considered taking into consideration that it will be located near an existing water canal?

My thinking is that being an structure where each wall is basically supported on three sides (side walls and bottom or top slab), the forces that should be considered are the at rest pressure. Please comment on any additional load to be considered.
 
If you are designing an concrete culvert, you should get a copy of AASHTO code, You will find all the info you need. actually there is a easy way to do it. DOT of your state or other state may have a free program for culvert design. it maybe free. the program manual will list all the items you need to check of course loads you use and how to model.... it helps?
 
I would consider the following load cases for an insitu constructed reinforced concrete chamber. However, can you use precast concrete rings as an alternative. PC are not 100% water tight but that might not be an issue for a well.


1) External pressure on walls from soil (At rest is conservative);
2) External water pressure;
3) Additional surcharge at ground level such as from traffic (construction or otherwise) or snow;
4) Flotation check to ensure structure is buoyant in a high water table, will induce additional loading in walls and base;
5) Internal water pressure with no backfill if you carry out a watertightness test;
6) Any construction loads depending on construction sequence;

If it is near to a canal you might also need to consider special durability requirements depending on whether the canal water is contaminated
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top