Vent Hole in HTHW Check Valve

Status
Not open for further replies.

steamdog

Chemical
Nov 18, 2008
111
Just curious about a specification I just saw. There is a control valve for a high temperature hot water heat exchanger (400 deg f at 400 psi design). They specified a vent hole in a check valve to be installed on the outlet side of the heat exchanger. Anyone know why?
 
Replies continue below

Recommended for you

I think it should read: "... vent hole and a check valve ..."
 
Two who are both guessing about this function.

Check valve and vent hole serve as a vacuum breaker for the HX. When HX cools down, shell will go below atmospheric pressure.....don't want to collapse the shell.
 
Thanks, Willard3
I did not think of a vacuum breaker. I suggest them all the time on steam heat exchangers so the condensate can drain, but it makes sense on water, too.
 