I'm curious , Can extended coverage sprinkler K11.2EC or K14.0EC install in pre-action system ?
Thank you for helping me.
Thank you for helping me.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Is there any specification in NFPA or FM DatasheetAs long as listed for use, yes. I have used plenty of EC sprinklers in preaction systems.
HC-3 production of plastic bag.What are you trying to protect?
Final product will stored on rack protect by ESFR K25.2 in other area , for raw materials in production process not exceed 1.8 meter in high and no more 64 sq.m (approximately four pallets) per 2.3.2 in FM, I can treat it as incidental storage to use Table 2.3.1.10 for protect this area.You need the manufactures data sheet for the specific sprinkler you are using,,,
Like this, read the listing and does and donts
Plus, I am not a FM person but you need to read the entire data sheet does and donts
Final product storage in the same building??? If so how high to the top of the storage?