I have a client that is wanting to install a 225lb heat pump above their unit. Metal deck, insulation, sheathing, membrane is the existing roof assembly.
I have been attempting to use a non-penetrating mount so that I don't have to deal with a phone call in a couple years because there is building envelope failure from 4 posts running down and attaching to the channels in their unit. There are a bunch of Unistrut style frames on the market that I want to attach to a wood framed platform (6x6 along the edges to accept screws from the metal frame above). The whole thing is to land on a big rubber mat to provide some friction resistance. With the added weight of the platform, I can't see this thing overturning or sliding under a realistic design load.
I am now realizing that the code won't allow me to use friction on its own to resist seismic loads. The platform will be almost adjacent to an existing fall arrest anchor. Can I attach a galvanized cable from the fall arrest anchor to the platform to provide that non-friction restraint? I need a sanity check.
Argument 1: Fall arrest can only be used as fall arrest alone.
Argument 2: It's a small unit with a nominal cable for seismic resistance. Fall arrest unlikely to be used during a seismic event. Maintenance schedule could be instituted so that the restraint cable is unhooked before and after window washing via the fall arrest anchor. Is this unreasonable?
Argument 3: The Code is the Code and the unit needs some sort of penetration to structure for seismic restraint.
With Argument 3, I think I would just go back to a steel system supported from the channels above the unit. It would require 4 penetrations through the roof, but ultimately provide the resistance required.
I'd be interested to know how others are handling this in their seismically active/inactive areas.
I have been attempting to use a non-penetrating mount so that I don't have to deal with a phone call in a couple years because there is building envelope failure from 4 posts running down and attaching to the channels in their unit. There are a bunch of Unistrut style frames on the market that I want to attach to a wood framed platform (6x6 along the edges to accept screws from the metal frame above). The whole thing is to land on a big rubber mat to provide some friction resistance. With the added weight of the platform, I can't see this thing overturning or sliding under a realistic design load.
I am now realizing that the code won't allow me to use friction on its own to resist seismic loads. The platform will be almost adjacent to an existing fall arrest anchor. Can I attach a galvanized cable from the fall arrest anchor to the platform to provide that non-friction restraint? I need a sanity check.
Argument 1: Fall arrest can only be used as fall arrest alone.
Argument 2: It's a small unit with a nominal cable for seismic resistance. Fall arrest unlikely to be used during a seismic event. Maintenance schedule could be instituted so that the restraint cable is unhooked before and after window washing via the fall arrest anchor. Is this unreasonable?
Argument 3: The Code is the Code and the unit needs some sort of penetration to structure for seismic restraint.
With Argument 3, I think I would just go back to a steel system supported from the channels above the unit. It would require 4 penetrations through the roof, but ultimately provide the resistance required.
I'd be interested to know how others are handling this in their seismically active/inactive areas.