Tx, folks. As "Feather" added, it is an open system, and as such subject to an equilibrium state with the environment. Hence, reactions are not "final".
CO2 <==> H2CO3 <==> NaHCO3 <==> Na2CO3
(Na+ could be replaced by 1/2 Ca++, 1/2 Mg++, etc)
Estimated pH ranges at which each forms of carbonate alkalinity are present are:
CO2 + H2O <--> H2CO3 pH: < 6.4
H2CO3 <--> (H+) + HCO3- pH: 6.4 - 10.33
HCO3- <--> (H+) + CO32- pH: > 10.33
One would expect an open cooling water system to already be at, or very very close to, equilibrium with CO2 in the atmosphere. The "energy" that "pushes" the CO2 to atmosphere is the very same "energy" used to "push" the CO2 into the cooling water ... the CO2 "doesn't water to be there" in the first place as it was already in equilibrium.
Adding CO2 shifts the equilibrium to the right ... but as the cooling water is in equilibrium with the atmosphere, if you wanted to reduce cooling water pH, increasing CO2 concentration of the air would be the answer!
Exception may be if the cooling water was significantly supersaturated with CO2. Since cooling tower's purpose is to bring air and cooling water into thermal equilibrium (much air-water contact), chemical equilibrium with air is also expected to result. Hence, loss of CO2 fed to cooling water, to atmosphere.
If you had enough CO2 to dissolve into the cooling water returning from the cooling tower to the heat exchange part of the system, making up for what is lost to atmosphere in each cooling water pass through the cooling tower, you could reduce pH that way, but only in the heat exchange part of the whole system. You lose pH control at the cooling tower and introduce dynamics to control of pH in the whole system.
Dissolving the CO2 into the water in the first place, would require a contacting system, as well, and high CO2 concentrations or pressures (which are assumed available). With the introduction of dynamics of CO2 dissolution, would pH be well controlled (eg: 8.3-8.7 pH units) throughout the cooling water system? pH too high at one location may cause scaling, pH too low at another location may cause corrosion. What is the cost of the contacting system?
"Feather"'s comment that the typical system is open, brings in the idea of closing the system. Perhaps, then, if one has enough waste CO2, vent it through cooling tower to increase the AIR's effective CO2 concentation (starting to "close" the system). This could save some sulfuric acid feed and sequester some greenhouse gas to the water (it may also increase evaporation by reducing the "air"'s relative humidity). However, this is likely very uneconomic. Sulpuric acid and its handling costs are generally quite low. Greenhouse gas sequestration is likely only temporary, as well (ie: when blowdown water returns from the cooling system to the environment, and comes into equilibrium with the environment).
If it was to be made to work, the new cooling water alakalinity equilibrium, and control of it, could adversely affect your cooling water treatment program. Even if CO2 control was good, CaCO3 concentration may rise, moreso than expected at observed pH. Water treatment chemical vendors may not find it economical to design treatment programs for such unusual conditions. Increased scale inhibiting polymer dosage, if required, could negate benefits of closing the sytem. Undiscovered increase in system scaling may further reduce ecomonics.
One may also need to consider the effect on cooling water system of any impurities in the CO2 stream.
Altering system temperature may also improve CO2 dissolution, but the tower's primary purpose is to provide economical cooling, so the practical benefit of temperature change is expected to be negligible, or negative.
In summary, feeding CO2 to reduce mineral acid feed to open cooling tower water systems appears to have some limited technical, and little, if any, economic, feasability. Indeed, it is likely very unecomonic.
You may find better uses for your CO2, such as neutralizing alkaline streams that are not already in equilibrium with CO2 in the atmosphere (eg:
If you decide to trial your process, it would be interesting to see results. For example, ability to economically maintain supersaturated CO2 concentrations in water would have interesting and widespread application. If it was possible, you'd think we would have heard of it already?
PS: Once through cooling water systems using alkaline water (eg: seawater) may be used to sequester CO2, but i think that this is a separate issue...
Wayne at