11echo
Petroleum
- Jun 4, 2002
- 444
I’ve got a question about using an existing vertical vessel (36” Dia. x 10’-0” S/S) …this is a 2 phase separator that deals with oil field production. We have a project that requires this vessel; it was originally built in 07, and is presently in “surplus”. Now vessel design is not my forte, but I’ve dealt with installing them for some time, I’m a Piping Designer.
I’m looking at some pictures of this thing, and I notice what I believe are a couple of issues! This vessel has a 36” Dia. skirt, about 2’-9” tall, I do NOT see any skirt vents (normally there are 4 near the top of the skirt), also there is only one access opening in the skirt, it is 10” Dia. there is a 2”-150#RF flange for a drain connection and it has a 7” projection vertically under the vessel, so the drain piping exits through the 10” access opening.
SO …it seems to me there is not large enough maintenance access to the drain flange under the vessel. AND without any skirt vents flammable or toxic gases could collection in the skirt. I’ve voiced my concerns to the project engineer, but he’s not a “bolts & nuts” type of guy …said he’s look into it. I’d like another opinion of any vessel experts so I can either agree or prepare to argue the point.
ALSO “IF” these items are required, would there be any issue retro-fitting them to the vessel without voiding the coded stamp? …THX!
I’m looking at some pictures of this thing, and I notice what I believe are a couple of issues! This vessel has a 36” Dia. skirt, about 2’-9” tall, I do NOT see any skirt vents (normally there are 4 near the top of the skirt), also there is only one access opening in the skirt, it is 10” Dia. there is a 2”-150#RF flange for a drain connection and it has a 7” projection vertically under the vessel, so the drain piping exits through the 10” access opening.
SO …it seems to me there is not large enough maintenance access to the drain flange under the vessel. AND without any skirt vents flammable or toxic gases could collection in the skirt. I’ve voiced my concerns to the project engineer, but he’s not a “bolts & nuts” type of guy …said he’s look into it. I’d like another opinion of any vessel experts so I can either agree or prepare to argue the point.
ALSO “IF” these items are required, would there be any issue retro-fitting them to the vessel without voiding the coded stamp? …THX!