I am not specifically familiar with the Moeller product, but I am familiar with products from Allen-Bradley and Group Schneider. These types of devices are not listed in the U.S. for use as circuit breakers, i.e., they are NOT UL 489 listed. They are only for use on grouped (or single) motor circuits when used in conjunction with an upstream UL 489 breaker or appropriate fuses. Newer products (Type E versions) have been approved as stand alone branch circuit protection for motor circuits only and meet UL 508 standards for industrial control panel installations. Rule of thumb: if it is not specifically listed for use on the application in question, it is not acceptable to the NEC.
Please search Allen-Bradley's site for Publication 1492-WP001A-EN-P for more info on UL 489, Ul 1077, and Type E devices.