Bill3752
Chemical
- Jan 24, 2008
- 138
I have recently sized several RV's using the unwetted wall equation. I have not included an environmental factor, F, as I do when doing wetted wall cases. In addition, the primary manufacturer software I am using does not allow F to be input. However, I just reread API 521, page 16, which states
"The discharge areas for .... on vessels containing supercritical fluids ... exposed to open fires can be estimated using equation 5 (F'A'/sqrt P). In the use of this equation, no credit has been taken for insulation. Credit for insulation may be taken per Table 5 (the environmental factor table)."
I am correct in assuming that I should be taking credit for insulation?
"The discharge areas for .... on vessels containing supercritical fluids ... exposed to open fires can be estimated using equation 5 (F'A'/sqrt P). In the use of this equation, no credit has been taken for insulation. Credit for insulation may be taken per Table 5 (the environmental factor table)."
I am correct in assuming that I should be taking credit for insulation?