And again:
Well, you can't believe everything that you read on the internet.
This link has the statement;
"Don't use zig-zag if possible."
For many years, the zig-zag was the standard connection used for single phase conversion.
The three phase to single phase conversion may be done with the zig-zag quickly and easily by moving one winding end from the neutral terminal to any other winding end. The wire numbers may be dirty, illegible or even missing. Only a simple continuity check is needed.
Link
Back to your question, reduced 120 Volt capacity.
In the series delta drawing, assume that the current rating of each winding is 100 Amps.
L1-L2 will supply 100 Amps at 240 Volts.
The windings, L1-L3-L2 will act as virtual winding with the same phase angle as L1-L2 (See Vector addition)
This virtual winding will Supply 100 Amps at 240 Volts in parallel with L1-L2
The total safe current available at 240 Volts is 200 Amps. (48000 VA or 48 KVA))
With a 120 Volt load, 100 amps will be supplied by the winding L1-N
100 Amps will be supplied by the winding combination L1-L3-L2-N
You may draw full current but the efficiency will be lower than with either the zig-zag or double delta connection.
100 Amps will be flowing through every winding.
With the double delta connection 100 Amps will be flowing in three windings.
With the zig-zag connection 100 Amps will be flowing through either two windings or 4 windings.
To anticipate your next question: 2/3 rating at single phase:
The series wye connection will support three 240 Volt circuits at 100 Amps each.
This will be 72000 VA or 72 KVA.
48KVA/72KVA = 2/3
With a 72 KVA machine at 80% PF, the prime mover will have enough power to develop 72KVA x 0.8 = 57.6 kW
When the machine is re-rated to 48 KVA, the output is KVA limited rather than kW limited. So kW may now equal KVA for 100% PF.
Bill
--------------------