There are two types of motors that are commonly applied to fans.
These are 1) high slip motors with a high resistance rotor, and 2) standard cage induction motors.
These motors behave totally differently under low voltage conditions.
High slip motors are commonly used on fans because they offer an easy means of speed control for the fan. With a high slip motor, as you reduce the voltage applied to the motor, the torque capacity reduces and the motor will slow. As the motor slows, the fan torque reduces and the motor will operate at a speed where the torque developed by the motor equals the torque required by the fan. I would expect the current to reduce wwhen the voltage reduces and there will be no issues arising from operating at the reduced voltage other than the air flow will be reduced.
A standard cage motor has a very low slip. As the voltage is reduced, the available torque will be reduced and the slip will increase. If the voltage is reduced sufficiently, the motor will stall and draw a very high current. This type of motor is not designed to be operated at reduced voltage and the reduction of voltage with a fan load will have a totally different result than the high slip motor. As the voltage is reduced, the speed will drop by a very small amount. The drop in fan load will be very small. The magnetising current in the motor will reduce. The load current however, will increase because the load will not change significantly.
Reducing the voltage on a standard motor that is well loaded, will result in an increase in current and an increase in slip power dissipated in the rotor.
Provided that the motor is operating at reduced load, there will be no damage to the motor. If however, the motor is operating at rated load, there will be increased motor heating which will accelerate the aging of the insulation within the motor due to elevated temperatures.
Bottom line? Fan motors (high slip motors) will not be affected. Standard motors will have increased heating which could cause early failure.
It is possible that the small motors will be fan motors, but the 200hp motor will be a standard motor.
The voltage drop from 380 to 340 is in the order of a 10% drop in voltage. This should not cause major issues with short term voltage sags.
Best regards,
Mark Empson