We have been installing 115 & 345 kV duct banks. Depth is 5 ft to bottom of trench, width on plans was 3 foot, but generally it will be wider to install conduit. (Depends on the ave. width of your local electrician). Generally power companies try to limit depth to 5 feet to reduce heat build up and reduce the need for shoring (OSHA limit). Typically duct will be 4 to 6 in. pvc poured with concrete to the top of the duct and backfilled with sand or flowable fill. In the old days cables ran at about 75 -80% of rated capacity and heat was not a problem. Today cables run much closer to 100% so heat is a big issue. To control this they use concrete and backfill with specific tested thermal properties. 94.5 is not a heavy line, but there may be some increase by the time it is installed as ACtrafficengr pointed out.
I would:
1. Ask the utility what they wanted as it will be there work.
2. Assume a 5x5 trench if you get no other information.
3. Keep crossing utilities 6 feet deep min. and parrallel utilities 5 ft away.
4. Accurately mark and map the utilties you install for this work. Monument above ground.
5 Cover utilites with a few inches of concrete, dye the top red and install narking tape. Be sure to use utility marking tape, as it partially metalic and will carry a tone for the mark out person.
6. Back chage the utility for the extra cost of the work. For example, Six foot of excavation will require shoring and additional excavation.
As for the vaults we are installing, they are huge. About 30 by 12 inside. We have also installed much smaller vaults so you really need to check with the utility on what they want. We are also istalling two redundant lines for the duct, complete with two sets of vaults at each location. Vaults are located about 1500 feet apart. This is due in part to the limitations on most cabe pulling equip.