Belz,
In addition to the previous comments I believe that condensation can be a concern in under floor systems if the cool plenum is suddenly exposed to warm, moist air. The dew point of the air entering the plenum must always be greater than the lowest temperature of any exposed surface within the plenum, otherwise condensation will occur. This phenomenon can be avoided if the plenum is well sealed against outside air infiltration, and if sudden step-changes in supply air conditions are avoided. For example, when the fan shuts down at the end of the day, warm and moist air should be blocked from rushing into the cool plenum. Similarly, during occupied hours, if the mechanical cooling abruptly shuts down and the dew point of the supply air suddenly rises, the fan may need to be shut off, or the outside air dampers adjusted. In addition, if your intention is to use the slab thermal reservoir to cool the space, for example, after the slab is “charged” with cool air at night, the mechanical system must be controlled to ensure that it does not supply air that exceeds the temperature of the coolest surface in the plenum. This can be a problem with systems installed over a slab on grade, since the slab temperature will be difficult to control, and condensation can occur.