- Apr 11, 2014
- 2
I know that unbraced lengths have been dealt with in these forums before. I think this situation is a little different from others I have seen posted here. In addition, my question is about the cantilevered section of a beam and not the back span. Hopefully we can avoid the whole inflection point argument.
I am analyzing an existing structure. There is a W24x55 girder that supports K joists at 6'-0" o.c. The K joists connect to the top of the W beam and there is metal deck on top of the joists. The W beam has a main span of 36' and cantilevers an additional 18' for a total length of 54'. The supporting columns are cantilevered with k=2.1. At the end of the cantilevered section of the beam, there is an existing masonry building. The metal deck connects to the masonry wall, but the W beam does not. The W beam has stiffener plates at the two column connections. There are no other lateral braces along the entire length of the beam.
Is the unbraced length of the cantilevered section of the W24x55 beam:
A. 6' since appendix 6.3.1 of the 13th edition AISC says to brace the top flange of cantilevers.
B. 18' since the stiffener plates at the column and K joist at the end of the cantilever effectively brace each other.
C. 36' (or 37.8') since the situation is analogous to a fixed / free column with k=2 (or k=2.1.)
D. 45' because the unbraced length is 2.5L from figure 5.11 of Galambos.
E. 135' because the unbraced length is 7.5L from figure 5.11 of Galambos.
F. Undefined (infinity) because there is no effective brace at either end of the cantilever.
G. Something else?
Thanks in advance for your insight.
I am analyzing an existing structure. There is a W24x55 girder that supports K joists at 6'-0" o.c. The K joists connect to the top of the W beam and there is metal deck on top of the joists. The W beam has a main span of 36' and cantilevers an additional 18' for a total length of 54'. The supporting columns are cantilevered with k=2.1. At the end of the cantilevered section of the beam, there is an existing masonry building. The metal deck connects to the masonry wall, but the W beam does not. The W beam has stiffener plates at the two column connections. There are no other lateral braces along the entire length of the beam.
Is the unbraced length of the cantilevered section of the W24x55 beam:
A. 6' since appendix 6.3.1 of the 13th edition AISC says to brace the top flange of cantilevers.
B. 18' since the stiffener plates at the column and K joist at the end of the cantilever effectively brace each other.
C. 36' (or 37.8') since the situation is analogous to a fixed / free column with k=2 (or k=2.1.)
D. 45' because the unbraced length is 2.5L from figure 5.11 of Galambos.
E. 135' because the unbraced length is 7.5L from figure 5.11 of Galambos.
F. Undefined (infinity) because there is no effective brace at either end of the cantilever.
G. Something else?
Thanks in advance for your insight.