Suggestion to Shortstub (Electrical) May 25, 2003 marked ///\\\
I hate to see this tread end with a zero (excuse the pun) for effort. Here is a simpler mathematical approach using trigonometry instead of additional measurement, and without symmetrical compomnents:
///Yes, indeed; however, it appears to be an approximate approach. The approximate approaches are o.k. if they satisfy the Client and hardware.\\1) Construct an uneven-sided triangle using the magnitudes of the original 'given' currents as sides. Let L1, L2, and L3 represent the annealer segment currents, i.e., 1,115 Amp, 1,078 Amp (including quench ground-return), and 1,092 Amp, respectively.
///Good; however, where is the 78A ground current?\\2) Label the interior angles, A, B, C, as follows:
A = the angle between sides L2 abd L3.
B = the angle between sides L1 and L2.
C = the angle between sides L3 and L1.
///O.k.\\3) Then, using the Law of Cosines results in the following values:
A = 59.70 deg.
B = 61.82 deg.
C = 58.40 deg.
///O.k.\4) Construct a phase-sequence diagram using L2 as reference. The resultant phasors are:
L1 = 1115A @ 118.2 deg (leads L2).
L2 = 1078A @ 0.0 deg.
L3 = 1092A @ 239.7 deg (lags L2).
///O.k.\\5) Calculate the corresponding transformer secondary line currents:
Ix1 = L2 - L1 = 1,882 @ -31.5 deg.
Ix2 = L1 - L3 = 1,926 @ +89.3 deg.
Ix3 = L3 - L2 = 1,882 @ -149.9 deg.
///O.k.\\6) Calculate the associated primary-side line currents using the turns ratio, i.e., n = sqrt(3)xN, the voltage ratio, as follows:
Ia = (1/n) x (Ix1 - Ix3) = 272A @ -0.7 deg.
Ib = (1/n) x (Ix3 - Ix2) = 277A @ -120 deg.
Ic = (1/n) x (Ix2 - Ix1) = 278A @ +119 deg.
///O.k. as far as the approximations are concerned. I also looked into the approximate shifts in currents on the secondary side, i.e. 0deg, 120deg and 240deg in:
"""jbartos (Electrical) Apr 25, 2003
Answers to gcaudill (Electrical) Apr 24, 2003 marked ////\\\jbartos wrote:
//(1115/0deg + 1000/120deg + 1092/240deg)/3=Io (is) different from zero. Therefore, the Ig is different from zero and equal to Ig=3Io, and Ix1+Ix2+Ix3=Ia+Ib+Ic=Ig different from zero at X2.//""""
However, I claim that the angles should be measured instead of approximated by 0deg, 120deg, 240deg, to have the problem well posed. Textbook examples are often given with the angles given. This is of course for students exercise only.\\A current balance check results in an almost equal primary and secondary loading of about 229 kVA.
///Good, up to "almost".\\Another check would be to determine the SCR firing angles for each phase and then calculate the equivalent resultant rms voltage.
///What about the angle shifts between Vab, Vbc and Vca?\\\