The unbalanced snow loads load requirements in ASCE 7-02 raises a lot of questions. Following the code in most cases when you have a gable roof you have a pretty severve unbalanced load requirement. ASCE 7-02 requires the application of unbalanced snow loads to situations where in Minnesota, in the past unbalanced snow would not have been considered.
In the past I considered unbalanced snow loads in systems where unbalanced loads would produce stress reversals in members. I would not have considered unbalanced loads in a gable roof with rafters and a ridge beam.
In the past I would have designed a building in out state Minnesota for 30 p.s.f. roof snow load. The firm I work for, in the past designed a very large number of structures in out state Minnesota using 2" mominal wood deck, rafters at 8' o.c. supported by a ridge beam, with a design snow load of 30 p.s.f. No unbalanced loads were considered.
Under the current State Code which follows ASCE 7, almost of those structures would not comply with the code. Yet they are still standing and performing well.
Those same structures if designed today would have to be designed for a basic snow load o f 42 p.s.f. and unbalanced snow load. This load would apply to the 2" deck, all the rafters and the ridge beam.
My opinion is that the new codes eliminate sound engineering judgement.